Using the Origin Variable

In servo control applications, the Command and Actual Positions for an Axis are generally used for position error calculations. On each sample, the controller reads the new Actual Positions from the feedback devices and calculates the new Command Positions.

To determine the relationship between Command and Actual Positions for an Axis and physical positions on the machine, you can use the Origin variable (which can be set by the host).

If it is important to set the Command or Actual Position to an exact value, you should use the mpiAxisOriginSet(...) function. Calling mpiAxisOriginSet(...) will modify both Command and Actual Positions by the same amount.

The Origin variable can be set in two different ways depending on the desired result. For example, assume the Command and Actual Positions are 10,000 and 10,024 counts respectively and that the axis is not moving.

Setting the Origin variable to 10,000 will result in Command Position = 0 and Actual Position = 24. Setting the Origin variable to 10,024 will result in Command Position = -24 and Actual Position = 0.

This second method is the most frequently used method for setting the new Origin after homing. Refer to the next table.

Position and Velocity criteria for generating motion completion events
If Command Position =
If Actual Position And you set Origin Variable Then Command Position =
And Actual Position =
10,000
10,024
10,000
0
24
10,000
10,024
10,024
-24
0

Cautions about motion in general:

  1. During motion, you should never call the mpiAxis[Actual|Command]PositionSet(...) or mpiAxisCommandOriginSet(...) functions.

  2. Setting a new Position using mpiAxisCommandPositionSet(...) or mpiAxisActualPositionSet(...) should be done with caution, because the controller will immediately try to servo to the new position. If the new and old command positions differ by a large amount the axis may fault (limit error) or jump to the new position at very high speed. Setting new positions with mpiAxisOriginSet(...) or mpiAxisCommandOriginSet(...) will not cause a jump.

  3. The effect of any origin or position set functions calls will not be seen by the host until the next controller sample following the call.

  4. Calling mpiAxisOriginSet() while an axis is in motion will change the final target position's value. This will not change the trajectory however. If the axis was to originally move 5000 counts, then the axis will still move a total of five thousand counts.
    Start
    Position
    Actual
    Position
    End
    Position
    Comment
    0
    0
    5000
    The beginning of a 5000 count move, origin currently 0.
    0
    2500
    5000
    Origin is about to be set to 2000.
    -2000
    500
    3000
    Origin has been changed to 2000.
    -2000
    3000
    3000
    Motion is complete. Distance traveled still 5000 counts.